Question 10016 of 731 · Texas Journeyman Electrician Exam
Over an outdoor pool, what is the minimum height of a luminaire or ceiling fan above the maximum water level?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10016
- A: 12 ft
Explanation
In outdoor pool areas, luminaires, lighting outlets, and ceiling-suspended paddle fans over the pool or within 5 ft horizontally of the inside walls must be at least 12 ft above the maximum water level. The height protects swimmers from contact with the equipment and from parts that could fall into the water.