Question 10031 of 731 · Texas Journeyman Electrician Exam
Pool water must be bonded by a conductive surface in contact with the water of at least what area?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10031
- A: 9 square inches
Explanation
Where none of the bonded parts is in direct contact with the pool water, an intentional bond of a conductive surface area of at least 9 square inches must be installed in contact with the water. The bond may be made with a listed fitting, a ladder anchor, or other approved means connected to the bonding grid.
More questions: Special Equipment, Pools, PV and EV
- 10032Metal parts such as fences or railings must be bonded when within what distance of the inside walls of a pool, unless separated by a permanent barrier?
- 10033A commercial spa requires an emergency shutoff for the recirculation and jet system. Where must it be installed?
- 10036How must a hydromassage bathtub be supplied?
- 10038For a fountain, which equipment requires GFCI protection unless it is listed for operation at low voltage?
- 10041Under NEC 2026, as amended by TIA 26-1, where may ground-fault protection NOT be installed for a variable-speed pool motor that uses an adjustable-speed drive?
- 10042A pool pump motor is connected to a single-phase, 240-volt, 20-ampere branch circuit. What protection is required for the outlet?