Question 11032 of 731 · Texas Journeyman Electrician Exam
What identification is required on the disconnecting means for a fire alarm branch circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11032
- B: Red identification and marking as a fire alarm circuit, accessible only to qualified personnel
Explanation
The location of the fire alarm branch-circuit OCPD must be permanently identified at the fire alarm control unit, and the disconnecting means must have red identification, be accessible only to qualified personnel, and be marked as a fire alarm circuit. This prevents unauthorized personnel from switching off the fire alarm system.