What is the line-to-neutral voltage of a 480Y/277 volt system, calculated from the 480 volt line-to-line value?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13020
- D: 277 V
Explanation
In a wye system the line-to-neutral voltage equals the line-to-line voltage divided by 1.732: 480 / 1.732 = 277 V. Halving the voltage (240 V) only works for a single-phase center-tapped system.
More questions: Electrical Calculations
- 13021Each winding of a balanced delta-connected load carries 20 amperes. What is the line current?
- 13022What is the apparent power of a three-phase 480 volt load drawing 100 amperes per line?
- 13023A plant load of 100 kW operates at 0.80 power factor. About how much capacitor kVAR is needed to raise the power factor to 0.95?
- 13024Resistors of 6, 3 and 2 ohms are connected in parallel. What is the total resistance?
- 13025A 10 ohm and a 15 ohm resistor are connected in parallel. What is the equivalent resistance?
- 13026A 4 ohm resistor is connected in series with a parallel group of 6 ohms and 12 ohms, and the circuit is supplied at 120 volts. What is the total current?