A 240 volt single-phase load of 40 A is located 180 feet from the panel. What is the smallest copper conductor that keeps voltage drop at or below 3 %?

Exactly one answer is correct.

Show solution

Correct answer to question 13035

  • C: 6 AWG

Explanation

Allowed drop is 0.03 x 240 = 7.2 V, so CM = 2 x 12.9 x 40 x 180 / 7.2 = 25,800 circular mils. 8 AWG (16,510) is too small, so 6 AWG (26,240) is required; leaving out the factor 2 wrongly points to 8 AWG.