Question 13065 of 731 · Texas Journeyman Electrician Exam

A box has a marked volume of 18.0 cubic inches and will contain only 12 AWG conductors with no fittings, devices or grounding conductors. What is the maximum number of conductors permitted?

Exactly one answer is correct.

Show solution

Correct answer to question 13065

  • A: 8

Explanation

Each 12 AWG conductor requires 2.25 cu in, so 18.0 / 2.25 = 8 conductors. Using the 14 AWG allowance of 2.0 cu in would wrongly give 9.

Next to question ›