Question 13077 of 731 · Texas Journeyman Electrician Exam
Using a 40 % fill area of 0.213 sq in for 3/4 inch EMT and an area of 0.0133 sq in for 12 AWG THHN, how many 12 AWG THHN conductors are permitted?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13077
- A: 16
Explanation
0.213 / 0.0133 = 16.0, so 16 conductors fit. Using the total area of 0.533 sq in instead of the 40 % area gives 40, which ignores the fill limit.
More questions: Electrical Calculations
- 13078How many 10 AWG THHN conductors (0.0211 sq in each) may be installed in 1/2 inch EMT, which has a 40 % fill area of 0.122 sq in?
- 13079Three 4 AWG THHN (0.0824 sq in each) and one 8 AWG THHN (0.0366 sq in) are to be installed in EMT. Which is the smallest trade size permitted? (40 % areas: 3/4 in 0.213, 1 in 0.346, 1-1/4 in 0.598 sq in)
- 13080What is the total cross-sectional area of six 10 AWG THHN (0.0211 sq in each) and three 8 AWG THHN (0.0366 sq in each) conductors?
- 130813/4 inch EMT has a 40 % fill area of 0.213 sq in and 14 AWG THHN has an area of 0.0097 sq in. How many 14 AWG THHN conductors are permitted when all conductors are the same size?
- 130821 inch EMT has a total internal area of 0.864 sq in. What is the maximum cross-sectional area of a single conductor installed in it?
- 13083A 25 hp, 460 volt, three-phase induction motor has a table full-load current of 34 A. What is the minimum ampacity of its branch-circuit conductors?