Question 13099 of 731 · Texas Journeyman Electrician Exam
Why does the full-load current from Table 430.250, rather than the motor nameplate current, determine motor branch-circuit conductor ampacity for a general-purpose motor?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13099
- C: 430.6(A)(1) requires the table values for conductor and short-circuit device sizing
Explanation
430.6(A)(1) requires the table currents for ampacity and short-circuit and ground-fault protection, while separate overload protection is based on the nameplate current. The tables do not include the 125 % factor.
More questions: Electrical Calculations
- 13100A 25 kVA single-phase transformer has a 480 volt primary and a 240 volt secondary. What are the full-load primary and secondary currents?
- 13101What is the full-load secondary current of a 75 kVA, three-phase transformer with a 208Y/120 volt secondary?
- 13102What is the full-load primary current of a 75 kVA, three-phase transformer with a 480 volt delta primary?
- 13103A 45 kVA, three-phase, 480 volt primary transformer (1,000 volts or less) is protected on the primary side only. What is the maximum primary overcurrent device, using the next-higher-standard-size note?
- 13104A single-phase transformer steps 480 volts down to 120 volts. If the primary current is 10 A, what is the secondary current (ignoring losses)?
- 13105A transformer has a turns ratio of 20 to 1 and a primary voltage of 2,400 volts. What is the secondary voltage?