Question 13120 of 731 · Texas Journeyman Electrician Exam
A 240 volt, single-phase, 2 hp motor has a table full-load current of 12 A at 230 volts. What is the minimum branch-circuit conductor ampacity?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 13120
- D: 15 A
Explanation
Motor branch-circuit conductors need 125 % of the table current: 12 x 1.25 = 15 A. 30 A would be 125 % of the 115 V current of 24 A.
More questions: Electrical Calculations
- 13121Three-phase 460 volt motors are rated 5 hp (7.6 A) and 3 hp (4.8 A). What is the minimum ampacity of a feeder supplying only these two motors?
- 13122A 9 kW, 480 volt, three-phase resistive heater is a continuous load. What is the minimum standard overcurrent device rating?
- 13123What is the inverse time breaker maximum for a 3 hp, 230 volt, single-phase motor (table FLC 17 A), allowing the next higher standard size?
- 13001A resistive heating element has a resistance of 15 ohms and is connected to 120 volts. What current does it draw?
- 13002A 4,800 watt resistive water heater is connected to a 240 volt single-phase circuit. What is the current?
- 13003What is the resistance of a 1,500 watt, 120 volt space heater element at its rated operating point?