A feeder supplies a continuous load of 160 A only. What is the minimum rating of the feeder OCPD, assuming standard equipment not rated for 100 percent operation?

Exactly one answer is correct.

Show solution

Correct answer to question 3035

  • B: 200 A

Explanation

The feeder OCPD must be at least 125 percent of the continuous load. 160 A times 1.25 is 200 A, which is a standard rating. See 215.3 and 240.6(A).