Under the 2026 NEC, a detached dwelling storage building has a wood floor framed 2 ft above grade and is not intended as a habitable room. Do its 125-volt receptacles require GFCI protection under 210.8(A)?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4011
- A: Yes, the at or below grade condition was removed for accessory buildings
Explanation
In the 2026 edition, garages became a separate list item and the accessory building item no longer depends on a floor at or below grade level. Storage and work type accessory buildings are covered regardless of floor elevation.