Question 4021 of 850 · Texas Journeyman Electrician Exam
For other than dwelling units, what is the maximum rating of a three-phase receptacle covered by the GFCI requirements of 210.8(B), on systems of 150 volts or less to ground?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4021
- A: 100 amperes
Explanation
210.8(B) includes three-phase receptacles rated 150 volts or less to ground and 100 amperes or less. This brings 208Y/120-volt three-phase receptacles in listed locations under the GFCI rule.