Under the 2026 NEC as published by NFPA, a new outdoor air conditioning condenser at a single-family dwelling is connected after September 1, 2026, on a 240-volt, 30-ampere circuit. What ground-fault protection is required?

Exactly one answer is correct.

Show solution

Correct answer to question 4034

  • C: GFCI protection, with a listed Class C SPGFCI permitted

Explanation

In the 2026 edition the HVAC exception to 210.8(F) expires September 1, 2026, so the outlet needs GFCI protection, and a listed Class C special purpose GFCI is permitted for listed HVAC equipment. Note: under the Texas adoption, TDLR extended the HVAC exception without an expiration date, so this outlet would not need GFCI in Texas.