Question 4087 of 731 · Texas Journeyman Electrician Exam
In a dwelling unit, a 30-ampere branch circuit is permitted to supply which of the following?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4087
- B: Utilization equipment such as a clothes dryer
Explanation
210.23 permits a 30-ampere branch circuit to supply fixed lighting with heavy-duty lampholders only in other than dwelling units, or utilization equipment in any occupancy. A dryer on a 30-ampere circuit is a typical example.
More questions: Branch Circuits, GFCI and AFCI
- 4088A branch circuit supplies a continuous load of 16 amperes and no noncontinuous load. What is the minimum conductor ampacity before any adjustment or correction?
- 4089A branch circuit supplies 24 amperes of continuous load and 6 amperes of noncontinuous load. What is the minimum standard overcurrent device rating?
- 4090For branch circuit sizing, a continuous load is one where the maximum current is expected to continue for how long?
- 4091When may a branch circuit overcurrent device be sized at 100 percent of the continuous load instead of 125 percent?
- 4094A multiwire branch circuit supplies receptacles in a dwelling. What does the NEC require at the point where the branch circuit originates?
- 4095A multiwire branch circuit in general may supply only which type of load?