Question 4093 of 931 · Texas Journeyman Electrician Exam
Tap conductors from a 50-ampere range branch circuit to a wall-mounted oven must have an ampacity of at least what value?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 4093
- D: 20 amperes
Explanation
210.19 permits tap conductors from a 50-ampere branch circuit supplying ranges, wall-mounted ovens and counter-mounted cooking units if they have an ampacity of at least 20 amperes. They must be sufficient for the load and not longer than needed for servicing.
More questions: Branch Circuits, GFCI and AFCI
- 4094A multiwire branch circuit supplies receptacles in a dwelling. What does the NEC require at the point where the branch circuit originates?
- 4095A multiwire branch circuit in general may supply only which type of load?
- 4096How must the conductors of a multiwire branch circuit be identified in a panelboard?
- 4097In a 120/240-volt, 3-wire multiwire branch circuit, why must the two ungrounded conductors be connected to opposite lines?
- 4098In a dwelling living room, what may substitute for the required wall-switch-controlled lighting outlet?
- 4099In which dwelling rooms is a switched receptacle NOT permitted as a substitute for the required wall-switch-controlled lighting outlet?