Why is the earth not permitted as the effective ground-fault current path?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5045
- A: Its impedance is too high to make OCPDs trip reliably
Explanation
The earth has high impedance, so a ground fault through earth may not draw enough current to open the OCPD. The Code requires a low-impedance metallic path instead. See 250.4(A)(5).