Question 5056 of 731 · Texas Journeyman Electrician Exam
The system bonding jumper of a separately derived system is sized based on
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 5056
- D: The derived ungrounded conductors and Table 250.102(C)(1)
Explanation
The system bonding jumper is sized like a main bonding jumper, using Table 250.102(C)(1) with the size of the derived ungrounded conductors. See 250.30(A)(1) and 250.28(D).
More questions: Grounding and Bonding
- 5057A detached garage supplied by a feeder must have a grounding electrode system, except where it is supplied by
- 5058At a separate building supplied by a feeder that includes an EGC, the grounded conductor at the building disconnect must be
- 5059Which of these AC systems is required to be grounded?
- 5060High-impedance grounded neutral systems are permitted for 3-phase AC systems of 480 V to 1000 V where
- 5061Which of the following shall NOT be used to connect EGCs or bonding jumpers to enclosures?
- 5062An equipment bonding jumper on the load side of an OCPD is sized according to