Question 6012 of 731 · Texas Journeyman Electrician Exam
When a cable is installed through a bored hole in a wood stud, how far must the edge of the hole be from the nearest edge of the stud unless a steel plate is used?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6012
- D: 1 1/4 in
Explanation
Holes in wood framing must be bored so the edge of the hole is at least 1 1/4 in from the nearest edge of the member. If that distance cannot be kept, the cable must be protected by a steel plate or sleeve. See 300.4 in NEC 2020 and 2023 (300.6 in NEC 2026).
More questions: Wiring Methods, Conductors and Boxes
- 6013NM cable passes through holes in metal studs that are punched at the factory. What must be done?
- 6014A cable run parallel to a wood framing member must be kept at least how far from the nearest edge of the member where nails or screws are likely to penetrate?
- 6017Where ungrounded conductors 4 AWG or larger enter an enclosure through a raceway, what is required at the entry?
- 6018NEC 2026 added a requirement in 300.4 for conductors and wiring methods that have been
- 6019EMT must be securely fastened within what distance of each outlet box, junction box, or termination?
- 6020What is the maximum distance between supports for EMT under the general rule?