Rigid metal conduit must generally be secured within what distance of each box or termination?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6021
- A: 3 ft
Explanation
RMC must be secured within 3 ft of each outlet box, junction box, device box, cabinet, conduit body, or other termination. The distance may be increased to 5 ft where structural members do not permit fastening within 3 ft. See 344.30(A).
More questions: Wiring Methods, Conductors and Boxes
- 6022Trade size 1 rigid PVC conduit must be supported at intervals not exceeding
- 6023Expansion fittings are required in a run of PVC conduit where the expected length change due to temperature is at least
- 6024NM cable must be secured at intervals not exceeding
- 6025NM cable must be secured within what distance of every cable entry into an enclosure such as an outlet box?
- 6027Type MC cable must generally be secured within 12 in of each box and at intervals not exceeding
- 6028Type AC cable must be secured within 12 in of each box and at intervals not exceeding