Question 6037 of 731 · Texas Journeyman Electrician Exam
What is the maximum percent fill of a conduit containing three or more conductors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 6037
- A: 40 percent
Explanation
Chapter 9, Table 1 limits conduit fill to 40 percent of the cross-sectional area for over two conductors. One conductor may fill 53 percent and two conductors 31 percent.
More questions: Wiring Methods, Conductors and Boxes
- 6038A conduit nipple not exceeding 24 in long between boxes may be filled to what percent of its area?
- 6039When calculating conduit fill, how are equipment grounding conductors treated?
- 6040What volume allowance does the box fill table assign to each 12 AWG conductor?
- 6041In a box fill calculation, a single receptacle on one yoke counts as
- 6042Two equipment grounding conductors enter a box. How are they counted for box fill?
- 6043A box contains four 12 AWG circuit conductors, two 12 AWG EGCs, and one switch on a single yoke. No clamps or fittings. What is the minimum box volume?