How is an isolated ground receptacle identified on its face?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7014
- B: An orange triangle
Explanation
Section 406.3(E) requires isolated ground receptacles to be identified by an orange triangle on the face. The grounding terminal of this device is insulated from the mounting yoke. NEC 2026 renumbered this rule within Article 406.