In a commercial building, a panelboard is supplied by a feeder from another panel. What must the panelboard be marked with?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7035
- D: The identification and location of the source that supplies it
Explanation
Section 408.4(B) requires panelboards and switchboards supplied by a feeder in other than one- or two-family dwellings to be permanently marked with where the power supply originates. This helps workers find the correct disconnect quickly.