Two 480 volt switchboards with exposed live parts face each other across an aisle (Condition 3). What is the minimum working space depth?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7063
- C: 4 ft
Explanation
Exposed live parts on both sides of the working space is Condition 3. For 151 to 600 volts to ground, Table 110.26(A)(1) requires a depth of 4 ft.