Under NEC 2026, from where is the depth of the working space in front of enclosed equipment measured?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 7068
- D: From the front cover of the enclosure
Explanation
NEC 2026 clarified that the depth of the working space is measured from the front cover of the enclosure rather than from the live parts inside. Equipment with a removable or hinged cover is therefore measured from the closed cover.