Question 8004 of 731 · Texas Journeyman Electrician Exam
Which value is used to size separate motor overload protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8004
- B: The motor nameplate full-load current
Explanation
Section 430.6(A)(2) requires separate motor overload protection to be based on the nameplate full-load current. Overloads must match the actual motor, while conductors and short-circuit protection use the table values.
More questions: Motors, HVAC, Generators and Transformers
- 8005A motor with a marked service factor of 1.15 needs a separate overload device. What is the maximum rating as a percentage of nameplate full-load current?
- 8006A motor is marked with a temperature rise of 40 degrees C. What overload rating is permitted as a percentage of nameplate current?
- 8007A motor has a service factor of 1.0 and no temperature rise marking. What is the maximum overload rating?
- 8008A motor with a service factor of 1.0 has a nameplate current of 20 A. What is the maximum separate overload setting under 430.32(A)(1)?
- 8009The overload selected at 125 percent is not enough to start a motor with a service factor of 1.15. What is the highest rating the next step permits?
- 8010How many overload units are required for a three-phase ac motor?