Question 8017 of 731 · Texas Journeyman Electrician Exam
A motor has a table full-load current of 22 A. Dual-element fuses are used for branch-circuit short-circuit protection. What is the maximum standard fuse size, applying the next higher size rule?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8017
- B: 40 A
Explanation
Table 430.52 allows 175 percent for dual-element fuses. 22 A times 1.75 equals 38.5 A, which is not a standard size, so the next higher standard size of 40 A is permitted.
More questions: Motors, HVAC, Generators and Transformers
- 8019Under NEC 2026, what may not be installed between the output terminals of power conversion equipment, such as a variable frequency drive, and the motor?
- 8020Where must a motor disconnecting means be located in relation to the motor and driven machinery?
- 8021What does the NEC mean when it says equipment is in sight from other equipment?
- 8022What is the minimum ampere rating of a motor disconnecting means for a motor rated 1000 volts or less?
- 8023A motor disconnect switch for a 10 hp motor must be rated in which unit?
- 8024How many conductors must a motor disconnecting means open?