Question 8025 of 731 · Texas Journeyman Electrician Exam
What must a motor disconnecting means clearly indicate?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8025
- C: Whether it is in the open (off) or closed (on) position
Explanation
Section 430.104 requires the disconnecting means to plainly indicate whether it is open or closed. A worker can then verify the motor is isolated before servicing it.