A transformer rated 1000 volts or less has primary protection only, and the primary current is 9 A or more. What is the maximum primary overcurrent device rating?

Exactly one answer is correct.

Show solution

Correct answer to question 8061

  • A: 125 percent of rated primary current

Explanation

Table 450.3(B) limits primary-only protection to 125 percent of the rated primary current when that current is 9 A or more. If 125 percent does not match a standard size, the next higher standard size is permitted.