Question 8061 of 731 · Texas Journeyman Electrician Exam
A transformer rated 1000 volts or less has primary protection only, and the primary current is 9 A or more. What is the maximum primary overcurrent device rating?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 8061
- A: 125 percent of rated primary current
Explanation
Table 450.3(B) limits primary-only protection to 125 percent of the rated primary current when that current is 9 A or more. If 125 percent does not match a standard size, the next higher standard size is permitted.