Question 9016 of 731 · Texas Journeyman Electrician Exam
Which wiring method is generally permitted in a Class I, Division 1 location?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9016
- C: Threaded rigid metal conduit
Explanation
Threaded rigid metal conduit and threaded steel intermediate metal conduit are the basic wiring methods for Class I, Division 1, along with certain listed cables such as Type MI and MC-HL. EMT, ENT, and Type NM cable are not permitted there.
More questions: Special Occupancies