Question 9031 of 731 · Texas Journeyman Electrician Exam
Branch circuits serving patient care spaces must provide two equipment grounding paths. Which combination meets this requirement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 9031
- C: A metal raceway or cable armor qualifying as an EGC plus an insulated copper equipment grounding conductor
Explanation
Wiring in patient care spaces must use a metal raceway or cable with a metal armor or sheath that qualifies as an equipment grounding conductor, and it must also contain an insulated copper equipment grounding conductor. This redundancy reduces shock risk to patients.
More questions: Special Occupancies
- 9035The essential electrical system of a hospital is divided into which branches?
- 9036Article 518 for assembly occupancies applies to buildings or portions of buildings designed for the gathering of how many persons or more?
- 9039At a carnival, circus, or fair, 125-volt, single-phase, 15- and 20-ampere receptacles used by personnel or readily accessible to the public require what protection?
- 9057On a construction site, a 125-volt, single-phase, 20-ampere receptacle on a temporary power pole used by workers requires what protection?
- 9058Temporary electrical power for holiday decorative lighting is limited to a maximum period of how many days?
- 9059When must temporary wiring installed for construction be removed?