When a copper grid is used for pool perimeter bonding, the conductors must form a grid with a uniform spacing of how much?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10028
- C: 12 in by 12 in
Explanation
A perimeter copper grid uses 8 AWG bare solid copper bonded at all crossings in a uniform 12 in by 12 in pattern, with a 4 in tolerance. It follows the contour of the perimeter surface.
More questions: Special Equipment, Pools, PV and EV
- 10030For conductive pool shells, perimeter surface bonding must attach to the structural reinforcing steel or copper grid at a minimum of how many points?
- 10031Pool water must be bonded by a conductive surface in contact with the water of at least what area?
- 10032Metal parts such as fences or railings must be bonded when within what distance of the inside walls of a pool, unless separated by a permanent barrier?
- 10033A commercial spa requires an emergency shutoff for the recirculation and jet system. Where must it be installed?
- 10034Receptacles in an indoor spa or hot tub area must be located at least how far from the inside walls of the spa or hot tub?
- 10035What protection is required for the outlet supplying a self-contained outdoor spa or hot tub?