Question 10039 of 931 · Texas Journeyman Electrician Exam
Under NEC 2026, which receptacles near a storable pool or fountain require ground-fault protection?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10039
- B: All receptacles within 20 ft of the inside walls
Explanation
NEC 2026 expanded 680.32 and 680.58 so that all receptacles within 20 ft of the inside walls of a storable pool or fountain must have ground-fault protection. Storable pools are often installed near existing outdoor receptacles, so this closes a common protection gap.