Question 10043 of 931 · Texas Journeyman Electrician Exam
Branch circuits for wet-niche pool luminaires must contain an insulated copper equipment grounding conductor of at least what size?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10043
- A: 12 AWG
Explanation
Wiring to underwater wet-niche luminaires must include an insulated copper equipment grounding conductor sized per 250.122 but not smaller than 12 AWG. A bare or aluminum EGC is not acceptable in this part of the installation.
More questions: Special Equipment, Pools, PV and EV
- 10044What is the maximum PV system voltage permitted for PV systems on one- and two-family dwellings?
- 10045What is the maximum PV system voltage on or in buildings other than one- and two-family dwellings?
- 10046A PV module has a short-circuit current (Isc) of 10 amperes. Using the standard method, what is the maximum circuit current for that PV circuit?
- 10047A single PV string has modules with an Isc of 10 amperes. What is the minimum conductor ampacity before adjustment and correction, applying both 125 percent factors?
- 10048A PV string has modules with an Isc of 8 amperes. What minimum OCPD rating is required if the circuit needs overcurrent protection, using both 125 percent factors and the next standard size?
- 10049Under PV rapid shutdown rules, conductors outside the array boundary must be reduced to no more than what voltage within 30 seconds of initiation?