A single PV string has modules with an Isc of 10 amperes. What is the minimum conductor ampacity before adjustment and correction, applying both 125 percent factors?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10047
- D: 15.6 amperes
Explanation
First the maximum current is 10 A x 1.25 = 12.5 A. Conductors must then carry 125 percent of that maximum current for continuous duty: 12.5 A x 1.25 = 15.6 A, which is the same as Isc x 1.56.