Question 10053 of 731 · Texas Journeyman Electrician Exam
A PV system has dc circuits operating at 80 volts or more between any two conductors. What protection is required?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10053
- C: Listed dc arc-fault circuit protection
Explanation
PV systems with dc circuits operating at 80 volts or greater between any two conductors must be protected by a listed PV arc-fault circuit interrupter or equivalent system. DC arcs are hard to extinguish and are a known cause of rooftop fires.