Question 10066 of 731 · Texas Journeyman Electrician Exam
An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10066
- B: 50 amperes
Explanation
The branch-circuit OCPD must be at least 125 percent of the maximum load: 40 A x 1.25 = 50 A. 50 A is a standard OCPD size.