The OCPD for a fire pump motor must be sized to carry what current indefinitely?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10076
- D: The locked-rotor current of the motor
Explanation
The OCPD for fire pump motors must be sized to carry the sum of the locked-rotor current of the motor and the full-load current of accessories indefinitely. The goal is to keep the pump running during a fire even if it is overloaded.