Under NEC 2026, fire pump supply and control conductors inside a building protected by concrete encasement require at least how much concrete?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10078
- D: 5 in
Explanation
NEC 2026 increased the concrete encasement requirement for fire pump supply and control conductors inside a building from 2 in to 5 in. These conductors moved from 695.6 to 695.7.