Question 10083 of 731 · Texas Journeyman Electrician Exam

A transformer arc welder has a rated primary current of 50 amperes and a 50 percent duty cycle. The I1eff value is not marked. Using a duty cycle multiplier of 0.71, what is the minimum supply conductor ampacity?

Exactly one answer is correct.

Show solution

Correct answer to question 10083

  • C: 35.5 amperes

Explanation

When I1eff is not given, the supply conductor ampacity is the rated primary current multiplied by the duty cycle factor: 50 A x 0.71 = 35.5 A. Applying a 125 percent factor here is a typical error.

Next to question ›