Question 10009 of 731 · Texas Journeyman Electrician Exam
When may an information technology equipment room use the special provisions of Article 645?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10009
- D: Only when all of the conditions listed in 645.4 are met
Explanation
Article 645 is optional and may be applied only if every condition in 645.4 is met, such as a disconnect per 645.10, dedicated HVAC, listed ITE, restricted occupancy, and fire-resistant separation. Otherwise the general requirements of Chapters 1 to 4 apply.