Question 10012 of 731 · Texas Journeyman Electrician Exam
What is the minimum horizontal distance from the inside wall of a permanently installed pool for a general purpose 125-volt receptacle?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10012
- A: 6 ft
Explanation
Receptacles are not permitted within 6 ft of the inside walls of a pool. Between 6 ft and 20 ft, 125-volt, 15- and 20-ampere receptacles require GFCI protection.
More questions: Special Equipment, Pools, PV and EV
- 10013125-volt, 15- and 20-ampere receptacles located within what distance of the inside walls of a pool require GFCI protection?
- 10014At a dwelling with a permanently installed pool, where must the required 125-volt, 15- or 20-ampere receptacle be located?
- 10016Over an outdoor pool, what is the minimum height of a luminaire or ceiling fan above the maximum water level?
- 10017In an indoor pool area, the minimum height for a luminaire over the pool may be reduced to what height if the luminaire is totally enclosed and GFCI protected?
- 10018Switching devices must be located at least how far horizontally from the inside walls of a pool, unless separated by a solid fence, wall, or permanent barrier?
- 10020Unless listed for a lesser depth, the top of the lens of a wet-niche luminaire must be at least how far below the normal water level?