Branch-circuit conductors supplying information technology equipment under Article 645 must have an ampacity of not less than what percentage of the total connected load?

Exactly one answer is correct.

Show solution

Correct answer to question 10011

  • B: 125 percent

Explanation

Branch-circuit conductors supplying one or more units of ITE must have an ampacity not less than 125 percent of the total connected load. ITE typically runs continuously.