Under NEC 2026, may a 50-ampere receptacle for EVSE be installed on a 40-ampere branch circuit as 210.24 would otherwise allow?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10073
- C: No, this is not permitted for EVSE
Explanation
NEC 2026 625.44 states that a 50-ampere rated receptacle shall not be installed on a 40-ampere branch circuit for EVSE. The receptacle and circuit must match the continuous charging load.
More questions: Special Equipment, Pools, PV and EV
- 10076The OCPD for a fire pump motor must be sized to carry what current indefinitely?
- 10078Under NEC 2026, fire pump supply and control conductors inside a building protected by concrete encasement require at least how much concrete?
- 10083A transformer arc welder has a rated primary current of 50 amperes and a 50 percent duty cycle. The I1eff value is not marked. Using a duty cycle multiplier of 0.71, what is the minimum supply conductor ampacity?
- 10084The OCPD for an arc welder may be rated at not more than what percentage of the rated primary current (I1max)?
- 10001Each commercial building and occupancy accessible to pedestrians must have at least one outlet for sign or outline lighting at each tenant entrance. What branch circuit must supply it?
- 10003What does Article 600 require of the disconnecting means for a sign?