Question 10072 of 731 · Texas Journeyman Electrician Exam
Under NEC 2026, a 50-ampere receptacle used for EVSE connection must meet which requirement?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10072
- A: It must be listed for EVSE use
Explanation
NEC 2026 625.44 requires 30-, 50-, and 60-ampere receptacles used for EVSE to be listed for EVSE use. This addresses overheating failures of general purpose receptacles under continuous charging loads.