An EVSE has a maximum load of 48 amperes. What is the minimum OCPD rating for the branch circuit supplying it?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10065
- B: 60 amperes
Explanation
EV branch circuits are sized for continuous duty, with an OCPD of not less than 125 percent of the maximum load: 48 A x 1.25 = 60 A. 60 A is a standard size.