Question 10068 of 731 · Texas Journeyman Electrician Exam
Indoor EV charging equipment is listed as requiring ventilation. What does the NEC require?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10068
- C: Mechanical ventilation interlocked with the equipment so charging only occurs while ventilation runs
Explanation
Where the EVSE is listed for charging vehicles that require ventilation indoors, mechanical ventilation must be provided and electrically interlocked with the equipment. The ventilation must operate throughout the charging cycle.
More questions: Special Equipment, Pools, PV and EV
- 10070Under NEC 2026, which EVSE requires a disconnecting means installed in a readily accessible location?
- 10072Under NEC 2026, a 50-ampere receptacle used for EVSE connection must meet which requirement?
- 10073Under NEC 2026, may a 50-ampere receptacle for EVSE be installed on a 40-ampere branch circuit as 210.24 would otherwise allow?
- 10076The OCPD for a fire pump motor must be sized to carry what current indefinitely?
- 10078Under NEC 2026, fire pump supply and control conductors inside a building protected by concrete encasement require at least how much concrete?
- 10083A transformer arc welder has a rated primary current of 50 amperes and a 50 percent duty cycle. The I1eff value is not marked. Using a duty cycle multiplier of 0.71, what is the minimum supply conductor ampacity?