Question 10064 of 731 · Texas Journeyman Electrician Exam
What protection is required for receptacles installed for the connection of EV charging equipment?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10064
- B: GFCI protection for personnel
Explanation
All receptacles installed for the connection of electric vehicle charging must have GFCI protection for personnel. EV charging is often done outdoors or in garages where moisture is common.
More questions: Special Equipment, Pools, PV and EV
- 10065An EVSE has a maximum load of 48 amperes. What is the minimum OCPD rating for the branch circuit supplying it?
- 10066An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?
- 10067How must each outlet installed for EVSE be supplied?
- 10068Indoor EV charging equipment is listed as requiring ventilation. What does the NEC require?
- 10070Under NEC 2026, which EVSE requires a disconnecting means installed in a readily accessible location?
- 10072Under NEC 2026, a 50-ampere receptacle used for EVSE connection must meet which requirement?