Question 10055 of 731 · Texas Journeyman Electrician Exam
A PV module has an open-circuit voltage (Voc) of 40 volts. Ten modules are connected in series, and the temperature correction factor for the lowest expected ambient temperature is 1.12. What is the maximum PV circuit voltage?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 10055
- C: 448 volts
Explanation
The maximum voltage is the sum of the series-connected Voc values corrected for the lowest expected ambient temperature: 40 V x 10 x 1.12 = 448 V. Dividing by the factor or ignoring it are typical errors.
More questions: Special Equipment, Pools, PV and EV
- 10056A PV module has a temperature-corrected Voc of 48 volts. What is the maximum number of modules that can be connected in series on a one- and two-family dwelling?
- 10064What protection is required for receptacles installed for the connection of EV charging equipment?
- 10065An EVSE has a maximum load of 48 amperes. What is the minimum OCPD rating for the branch circuit supplying it?
- 10066An EVSE is rated 40 amperes continuous. What is the minimum OCPD rating for its branch circuit?
- 10067How must each outlet installed for EVSE be supplied?
- 10068Indoor EV charging equipment is listed as requiring ventilation. What does the NEC require?