Correct answer to question 1093
- D: An overload
Explanation
Article 100 defines overload as operation in excess of normal full-load rating, or of a conductor in excess of its ampacity, that causes damage or overheating if it lasts long enough. A short circuit or ground fault is not an overload.
More questions: Definitions, Theory and Plans
- 1094Under the NEC, a disconnect is considered in sight from the equipment it serves when it is visible and not more than:
- 1095A branch circuit with two or more ungrounded conductors having a voltage between them and a grounded conductor with equal voltage to each ungrounded conductor is a:
- 1096A building-supplied transformer whose secondary has no direct electrical connection to the supply conductors, except through grounding and bonding connections, creates:
- 1097The point of connection between the facilities of the serving utility and the premises wiring is called the:
- 1098A partially protected location under a canopy or a roofed open porch is classified in the NEC as a:
- 1103NEC 110.3(B) requires that listed or labeled equipment be installed and used: