Which statement about branch circuits supplying fire alarm equipment is correct?
Exactly one answer is correct.
You got of questions right. Here on the question pages nobody remembers which ones you got wrong. The trainer saves your progress and asks the mistakes again until they stick.
Or free: the 10 questions most people get wrong
Show solution
Correct answer to question 11031
- D: They must not be supplied through GFCI or AFCI devices
Explanation
Branch circuits supplying fire alarm equipment must not be supplied through ground-fault or arc-fault circuit interrupters. A nuisance trip could disable the fire alarm system.